post #1 of 76 Old 04-12-2016, 10:24 PM Thread Starter
Senior Member
 
Bluefilosoff's Avatar
 
Join Date: Mar 2013
Posts: 101
View Bluefilosoff's Photo Album My Photos
20 amps at 110 volts Bandsaw

I want to order a 17" bandsaw and I am concerned about whether it needs a dedicated outlet like an electric stove or dryer or can I just plug it into an ordinary outlet and go?
The brochure says 20 amps at 110 volts or 10 amps at 220 volts? Any guidance greatly appreciated.
Bluefilosoff is offline  
Sponsored Links
Advertisement
 
post #2 of 76 Old 04-12-2016, 10:27 PM
Wood machinist
 
difalkner's Avatar
 
Join Date: Nov 2011
Location: NW Louisiana
Posts: 3,290
View difalkner's Photo Album My Photos
If it were mine I would wire it for 220 v and put it on a dedicated circuit. But definitely a dedicated circuit whichever way you go.
GuitarPhotographer likes this.

David

Curly Wood Shop on Etsy
David Falkner - Woodworking YouTube channel
Our music at church - current videos Airline Baptist BC Facebook Live
Romans 3:23
difalkner is offline  
The Following User Says Thank You to difalkner For This Useful Post:
Bluefilosoff (04-12-2016)
post #3 of 76 Old 04-12-2016, 10:37 PM
Senior Member
 
hwebb99's Avatar
 
Join Date: Nov 2012
Posts: 2,881
View hwebb99's Photo Album My Photos
I'd wire it 220. Due to lack of space in in my breaker box I only have two 220 volt circuits shared between 3 tools. It really isn't a big deal.
hwebb99 is offline  
The Following User Says Thank You to hwebb99 For This Useful Post:
Bluefilosoff (04-12-2016)
Sponsored Links
Advertisement
 
post #4 of 76 Old 04-12-2016, 10:43 PM Thread Starter
Senior Member
 
Bluefilosoff's Avatar
 
Join Date: Mar 2013
Posts: 101
View Bluefilosoff's Photo Album My Photos
Thanks, I guess what I'm explaining poorly is can I run a saw that big on a household plug? I run an old Sears contractor saw and a 6 " Laguna jointer on separate household plugs and I'm wondering if I could get away with that for a bigger bandsaw like I'm considering.
Bluefilosoff is offline  
post #5 of 76 Old 04-12-2016, 10:58 PM
Senior Member
 
Join Date: Aug 2012
Location: British Columbia, Canada
Posts: 4,986
View FrankC's Photo Album My Photos
Do you have 20 amp 110 outlets wired into your shop, most ordinary outlets are 15 amp.

If not you will have to run a new line to run the saw, in that case you might as well run a 220 circuit.

“Everything we hear is an opinion, not a fact. Everything we see is a perspective, not the truth.”
― Marcus Aurelius
FrankC
http://sawdustmaking.com
FrankC is offline  
post #6 of 76 Old 04-12-2016, 11:00 PM
No Longer Here
 
Join Date: Dec 2010
Location: God's beautiful hills of Middle Tennessee
Posts: 2,381
View Tennessee Tim's Photo Album My Photos
Not necessarily.... some 110 circuits are wired for 15 amps. And yes for safety it would be best as a dedicated 20 amp circuit BUT BEST if wired 220. this saves electricity and is easier on the motor during starting and operating.
Tennessee Tim is offline  
The Following User Says Thank You to Tennessee Tim For This Useful Post:
Bluefilosoff (04-12-2016)
post #7 of 76 Old 04-12-2016, 11:01 PM Thread Starter
Senior Member
 
Bluefilosoff's Avatar
 
Join Date: Mar 2013
Posts: 101
View Bluefilosoff's Photo Album My Photos
Quote:
Originally Posted by FrankC
Do you have 20 amp 110 outlets wired into your shop, most ordinary outlets are 15 amp. If not you will have to run a new line to run the saw, in that case you might as well run a 220 circuit.
Ah I see now, unfortunately just 15 amp so yes time to call sparky.

Cheers.
Bluefilosoff is offline  
post #8 of 76 Old 04-12-2016, 11:39 PM
Senior Member
 
hwebb99's Avatar
 
Join Date: Nov 2012
Posts: 2,881
View hwebb99's Photo Album My Photos
I doubt the saw would run on a 20 amp 110 volt breaker anyway. Have sparky wire it 220. It isn't that hard. You could probably do it yourself and save $.
hwebb99 is offline  
The Following User Says Thank You to hwebb99 For This Useful Post:
Bluefilosoff (04-12-2016)
post #9 of 76 Old 04-12-2016, 11:44 PM
Senior Member
 
Tony B's Avatar
 
Join Date: Jul 2008
Location: Dickinson, Tx. / Denison, TX
Posts: 3,145
View Tony B's Photo Album My Photos
DEpending on how far away your dryer outlet is, you can make a heavy duty extension cord and plug it in the dryer outlet when it is no being used. I did that for over a year and it worked out just fine.
Just make sure you rewire your motor for the 220V. There should be a name plate on the motor with some specs and a wiring diagram to rewire the motor for 220. Very easy to do.

Tony B



Retired woodworker, amongst other things, Sold full time cruising boat and now full time cruising in RV. Currently in Denison, Tx
Tony B is offline  
post #10 of 76 Old 04-12-2016, 11:55 PM Thread Starter
Senior Member
 
Bluefilosoff's Avatar
 
Join Date: Mar 2013
Posts: 101
View Bluefilosoff's Photo Album My Photos
Quote:
Originally Posted by Tony B
DEpending on how far away your dryer outlet is, you can make a heavy duty extension cord and plug it in the dryer outlet when it is no being used. I did that for over a year and it worked out just fine. Just make sure you rewire your motor for the 220V. There should be a name plate on the motor with some specs and a wiring diagram to rewire the motor for 220. Very easy to do.
Love this!

Good old fashioned woodworker resourcefulness. In a pinch I will do this until I get a line put in.
Thanks mang!
Bluefilosoff is offline  
post #11 of 76 Old 04-13-2016, 07:00 AM
Senior Member
 
Join Date: Sep 2011
Posts: 25,986
View Steve Neul's Photo Album My Photos
If it actually draws 20 amps on 110V you might have to put it on a dedicated line anyway. If you are at the saw for very long especially if you have anything else on the line running you shouldn't draw more than 16 amps on a 20 amp breaker. The general rule is to limit the draw to 80% of what the breaker is rated at. If it were me I would wire it to 220 but if that isn't an option I would change the wire to 10 gauge and install a 30 amp breaker.
Willy-N likes this.
Steve Neul is offline  
post #12 of 76 Old 04-13-2016, 07:29 AM
Senior Member
 
Join Date: Jul 2008
Location: Florida Panhandle
Posts: 11,646
View GeorgeC's Photo Album My Photos
Quote:
Originally Posted by hwebb99 View Post
I doubt the saw would run on a 20 amp 110 volt breaker anyway. Have sparky wire it 220. It isn't that hard. You could probably do it yourself and save $.
"You could probably do it yourself and save $"

I do not think you should do this. Hire a professional. From your post it does not appear that work of this type in is your wheelhouse.

George
Tony B likes this.
GeorgeC is offline  
post #13 of 76 Old 04-13-2016, 07:46 AM
Senior Member
 
Tony B's Avatar
 
Join Date: Jul 2008
Location: Dickinson, Tx. / Denison, TX
Posts: 3,145
View Tony B's Photo Album My Photos
[QUOTE=GeorgeC;1342857]................. i do not think you should do this. Hire a professional. From your post it does not appear that work of this type in is your wheelhouse..../QUOTE]

I totally agree with George. This is not meant to be a disparaging remark, but it is a humorous expression and mainly, it drives the point home.

Tony B



Retired woodworker, amongst other things, Sold full time cruising boat and now full time cruising in RV. Currently in Denison, Tx
Tony B is offline  
post #14 of 76 Old 04-13-2016, 07:47 AM
Senior Member
 
ducbsa's Avatar
 
Join Date: Jul 2014
Location: Virginia
Posts: 348
View ducbsa's Photo Album My Photos
+1 on a new 220v circuit.

Regarding lower powered 110v tools, how often do you run more than one at once? Even in industrial power distribution design, if the motors aren't always running, the cable and fuses are sized for less than the motor nameplate amp total.
ducbsa is offline  
post #15 of 76 Old 04-13-2016, 08:07 AM
Senior Member
 
Join Date: Jan 2010
Location: NW Pa
Posts: 2,841
View TimPa's Photo Album My Photos
if the motor is dual voltage (110v/220v) then you have the choice to run the tool on the 110v/20amp circuit, or a 220v/10a circuit.


a "typical" outlet circuit will have: 20 amp circuit breaker, 12 ga wire, and a 15 amp receptacle. after you verify the cb and wire, you should change the recep out for a 20 amp version to have a supply circuit capable of 20 amps for this tool.


Quote:
Originally Posted by Steve Neul View Post
If you are at the saw for very long especially if you have anything else on the line running you shouldn't draw more than 16 amps on a 20 amp breaker. The general rule is to limit the draw to 80% of what the breaker is rated at.
this is for branch circuits feeding continuous loads, which are on for >3 hours time. not to say that you couldn't derate all branch ckts for an element of safety.

Last edited by TimPa; 04-13-2016 at 08:11 AM.
TimPa is offline  
post #16 of 76 Old 04-13-2016, 08:36 AM
Senior Member
 
Join Date: Sep 2011
Posts: 25,986
View Steve Neul's Photo Album My Photos
Quote:
Originally Posted by TimPa View Post
if the motor is dual voltage (110v/220v) then you have the choice to run the tool on the 110v/20amp circuit, or a 220v/10a circuit.


a "typical" outlet circuit will have: 20 amp circuit breaker, 12 ga wire, and a 15 amp receptacle. after you verify the cb and wire, you should change the recep out for a 20 amp version to have a supply circuit capable of 20 amps for this tool.



this is for branch circuits feeding continuous loads, which are on for >3 hours time. not to say that you couldn't derate all branch ckts for an element of safety.
That's all fine on paper but it makes a difference if you are aggravated by running back and forth to the breaker box resetting it. Putting a 20 amp saw on a 20 amp circuit is pushing limits.
Tony B and Willy-N like this.
Steve Neul is offline  
post #17 of 76 Old 04-13-2016, 09:08 AM
Senior Member
 
Tony B's Avatar
 
Join Date: Jul 2008
Location: Dickinson, Tx. / Denison, TX
Posts: 3,145
View Tony B's Photo Album My Photos
Quote:
Originally Posted by Steve Neul View Post
.........Putting a 20 amp saw on a 20 amp circuit is pushing limits.
When in doubt, feel the wires, especially at the plug end. Slightly warm is not bad, but keep checking it. Hot is never good.
Also keep in mind that as the wires get warm, their electrical resistance gets higher. This results in even more warming. It becomes a system that feeds on itself. Either the wire, the fuse, the tool or all 3 are going die a painful death.

I still maintain that the safest cure is to use the 220V dryer outlet. That way when you pull the dryer plug, it cant be used at the same time as the saw. This is very safe. The only down side is the connecting and disconnecting of the new extension cord being a PITA. Then again, most woodworkers dont spend a lot of time on a band saw.

The plugs for the dryer outlet can be found in Walmart, Home Depot, Lowes and just about any hardware store. I havent bought any on a long time so I will guess the plug to cost around $15 or less these days.

Tony B



Retired woodworker, amongst other things, Sold full time cruising boat and now full time cruising in RV. Currently in Denison, Tx

Last edited by Tony B; 04-13-2016 at 09:15 AM.
Tony B is offline  
post #18 of 76 Old 04-13-2016, 09:11 AM
Senior Member
 
Join Date: Jan 2010
Location: NW Pa
Posts: 2,841
View TimPa's Photo Album My Photos
a proper 20 amp circuit is designed to supply a 20 amp load safely, with no overload conditions. if the over current protection device is tripping, there is an issue with the device and it should be looked at for a problem.
TimPa is offline  
post #19 of 76 Old 04-13-2016, 09:23 AM
Senior Member
 
Tony B's Avatar
 
Join Date: Jul 2008
Location: Dickinson, Tx. / Denison, TX
Posts: 3,145
View Tony B's Photo Album My Photos
Quote:
Originally Posted by Tony B View Post
When in doubt, feel the wires, especially at the plug end. Slightly warm is not bad, but keep checking it. Hot is never good.
Also keep in mind that as the wires get warm, their electrical resistance gets higher. This results in even more warming. It becomes a system that feeds on itself. Either the wire, the fuse, the tool or all 3 are going die a painful death.

I still maintain that the safest cure is to use the 220V dryer outlet. That way when you pull the dryer plug, it cant be used at the same time as the saw. This is very safe. The only down side is the connecting and disconnecting of the new extension cord being a PITA. Then again, most woodworkers dont spend a lot of time on a band saw.

The plugs for the dryer outlet can be found in Walmart, Home Depot, Lowes and just about any hardware store. I havent bought any on a long time so I will guess the plug to cost around $15 or less these days.
If your dryer is not in constant use, you might see about doing the same set-up for your Table saw, if it can be rewired for 220v also.

When you make the extension cord for the 220V you will be using a dryer plug at one end. I would strongly urge you to change the 110V ends of both the cord and the tool. There are less expensive 220v plugs both male and female that can be used at the tool end. This will elimate any chance of accidentally plugging a 220V plug into a 110V socket or outlet because the less expensive 220v plugs and recepticals will not fit in a 110v socket. The pin configuration is different.

Tony B



Retired woodworker, amongst other things, Sold full time cruising boat and now full time cruising in RV. Currently in Denison, Tx
Tony B is offline  
post #20 of 76 Old 04-13-2016, 09:55 AM
Sawdust Creator
 
ryan50hrl's Avatar
 
Join Date: Jun 2012
Posts: 8,047
View ryan50hrl's Photo Album My Photos
Quote:
Originally Posted by Steve Neul View Post
That's all fine on paper but it makes a difference if you are aggravated by running back and forth to the breaker box resetting it. Putting a 20 amp saw on a 20 amp circuit is pushing limits.

Putting a 20 amp saw in a home shop on a 20 amp circuit is by no means pushing it. That saw will rarely ever see full amp draw, and when it does, it will be for a short amount of time.

I have all of my circuits in my shop sized correctly, 15 amp circuits with 15 amp or less tools and 20 amp circuits for 15-20 amp tools. The only time I've EVER popped a breaker is when I stalled my RAS in really thick oak.

No ones hobby shop is ever going to have the tools running at 100% draw for hours on end.

I'm a firm believer that running a 30 amp circuit when a 20 amp circuit meets the requirements is a waste of money.

The tools don't make the craftsman....
ryan50hrl is offline  
Reply

Quick Reply
Message:
Options

Register Now



In order to be able to post messages on the Woodworking Talk - Woodworkers Forum forums, you must first register.
Please enter your desired user name, your email address and other required details in the form below.

User Name:
Password
Please enter a password for your user account. Note that passwords are case-sensitive.

Password:


Confirm Password:
Email Address
Please enter a valid email address for yourself.

Email Address:
OR

Log-in










Thread Tools
Show Printable Version Show Printable Version
Email this Page Email this Page
Display Modes
Linear Mode Linear Mode



Similar Threads
Thread Thread Starter Forum Replies Last Post
Bandsaw Box videos Bob Ross 2.0 Project Showcase 1 03-23-2016 11:39 PM
Bandsaw versus table saw AND planer? JimGnitecki Power Tools & Machinery 50 01-10-2016 11:02 PM
Bandsaw help Toolman50 Power Tools & Machinery 7 12-23-2015 11:42 PM
Good Bandsaw? Nathan Vaughan Power Tools & Machinery 8 11-10-2015 07:47 PM
Cut circles on the bandsaw? deadherring General Woodworking Discussion 8 08-04-2015 08:03 AM

Posting Rules  
You may post new threads
You may post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off

 
For the best viewing experience please update your browser to Google Chrome